• Constant Voltage Transformers

    From G8MNY@4:902/6 to WW on Wed Dec 11 05:57:59 2024

    To : TECH@WW

    By G8MNY (Updated Oct 07)
    (8 Bit ASCII graphics use code page 437 or 850, Terminal Font)

    Here is information about the principle of tuned saturated transformer type, of constant voltage mains transformer for power conditioning. This is not the same as the modern uninterruptable battery SM mode (RF generators) fast inverters that fill in holes in the mains, but a far simpler highly reliable passive system.

    MAGNETIC SATURATION
    Flux _____
    IRON ³ _.-~~/'~ The BH curve shows the magnetic
    LAMINATE ³./' ./' flux B saturate & flattens off as
    ./³ ./ the magnetising effort in Amp Turns
    ÄÄÄÄÄÄÄÄÄ/ÄÄÅÄÄ/ÄÄÄÄÄÄÄÄÄ +H increases. This is the heart of the
    ./' ³/' Amp Turns regulation principle.
    ./' _./'³
    _.:..-" ³-B
    ~~~~
    The transformer secondary it tuned with a capacitor, & it literally sucks all the power it can from the nearby primary magnetic circuit until the tuned core is saturated.

    2 MAGNETIC CIRCUITS
    Unlike a conventional transformer the primary & secondary are on different bobbins (coil formers) & are not tightly magnetically coupled. There is a magnetic filler piece put in between 2 bobbins typically with an air gap.
    ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ¿
    Simple CVT ³ ÚÄÄÄ¿ ÚÄÄÄ¿ ³
    ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ¿ ³ ³T~~~~~~~~~T³ ³
    ³ ÚÄÄÄ¿ ÚÄÄÄ¿ ³ ³ ³|BUCK COIL|³ ³
    ³ ³T~~~~~~~~~T³ ³ ³ ³ÏÍÍÑÍÍÍÑÍÍϳ ³
    ³ ³| TUNED & |³ ³ ³ ³ \_/ Gap³ ³ More Complex
    ³ ³| LOAD |³ ³ Specially ³ ³ ³\_/³ ³ ³ "ADVANCE"
    ³ ³| BOBBIN |³ ³ shaped ³ ³T~~~~~~~~~T³ ³ CVT
    ³ ³ÏÍÍÑÍÍÍÑÍÍϳ ³ transformer ³ ³| TUNED & |³ ³
    ³Gap~~³³ ³³~~Gap³ laminates. ³ ³| LOAD |³ ³
    ³ ÚÄÄÙ³ ³ÀÄÄ¿ ³ ³ ³ÏÍÍÑÍÍÍÑÍÍϳ ³
    ³ ³T~~~~~~~~~T³ ³ ³Gap~~³³ ³³~~Gap³
    ³ ³| MAINS |³ ³ ³ ÚÄÄÙ³ ³ÀÄÄ¿ ³
    ³ ³| BOBBIN |³ ³ ³ ³T~~~~~~~~~T³ ³
    ³ ³ÏÍÍÑÍÍÍÑÍÍϳ ³ ³ ³| MAINS |³ ³
    ³ ~~~ ~~~ ³ ³ ³ÏÍÍÑÍÍÍÑÍÍϳ ³
    ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙ ³ ~~~ ~~~ ³
    ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙ
    ELECTRICAL CIRCUITS
    For employment inside equipment __
    the secondary load windings are ==||( ³ 50Hz
    wound with the tuned circuit ÄÄÄÄÄÄ¿ || ||( === tuned
    winding. 50Hz )|| ||(__³ winding
    The power flowing in the tuned Supply )|| || _____
    winding must equal the maximum )|| ||( Regulated
    load for the system to regulate. ÄÄÄÄÄÄÙ || ||(_____ Secondary
    With fairly fixed loads this || || _____ Windings
    simple circuit will do. ==||(_____ Outputs

    Specialist regulation transformers with greater regulation demands & changing loads use bucking arrangements to improve the regulation.

    ADVANCE 1004 CVT
    ______ ÚÄÄÄÄÄÄÄ¿ 50Hz Tuned
    |Ú-ÂÂ-¿|( 620V ³ 1kW of power!
    || || ||( Buck ³
    ÄÄÄÄÄ¿ || || ||(_Coil === 24uF
    50Hz )|| |Æ µ| _³ ³ 660V AC
    180- )||gaps||( 600V ³
    270V )|| || ||( ³
    ÄÄÄÄÄÙ || || ||(_ÚÄÄÄÄÄÄ)ÄÄÄÄÄÄ>L
    || || ||( 245V ³ Fully Isolated &
    |À-ÁÁ-Ù|( ³ Regulated power
    ³~~~~~~ ÀÄÄÄÄÄÄÄÁÄÄÄÄÄÄ>N
    ³
    ÄÄÄÄÄÄÄÁÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ>E

    REGULATION

    Output ADVANCE Type 1004
    Volts
    /³\ /
    250´ /
    ³ No Load /_ _ . - - O/P 244V ñ2.5V for ñ40V I/P
    245´ _ . - Ä ' ~ /_ _ . . -
    ³ _ . - ~ _ . - Ä ~ / O/P 240V ñ3V for ñ40V I/P
    240´- ~ _ . - ~ /
    ³. - ~ @ 500W Load / _ . - Ä
    235´ ./- ' ~ O/P 230V ñ5V for ñ40V I/P
    ³ _.- ~ /
    230´ _. -~ /WITH
    ³ .-~ /NO CVT
    225´ .ú'@ 1kW Load /
    ³ / /
    220ÅÄÄÄÂÄÄÄÂÄÄÄÂÄÄÄÂÄÄÄÂÄÄÄÂÄÄÄÂÄÄÄÂÄÄÄÂÄ>Input
    180 190 200 210 220 230 240 250 260 270 Volts

    The regulation only occurs of course at the resonant frequency. The output is a fairly low distortion sine wave but not that good. Note that the output rapidly drops with the heavy overload, & in fact overloads tend to give a fairly safe constant current at just over the maximum current rating.

    IN USE
    Although they are very useful for ensuring the correct voltage, more & more equipment is immune to small power line fluctuations, except extreme voltages, so the need for a CVT is less apparent today.

    They are not so useful for computer kit as you might think, as the power off through one, causes the supply to fail over a few cycles, exactly the brown out synareo that can damage data on computers! Also the very high power TURN ON surge of a CRT screen power (e.g. 100W screen running but a 4kW surge) ensures a glitch will be caused on a low power CVT if the CRT is on the same CVT as the processor.

    They are also not much use on a generator supply, unless the frequency is fairly close to 50Hz for it to function properly.

    Power efficiency is also not good at about 10% of the full load is lost all the time as heat.

    I have used the 1kW one for /P OK, on a VERY long multiple spurred mains feed (1km) where the mains was liable to be all over the place. The isolation was
    an added safety feature, as too was the RF mains isolation.

    Site 1km tapped long cable 180-240V?
    Mains ÄÄÄÄÂÄÄÄÄÄÄÂÄÄÄÄÄÄÂÄÄÄÄÄÄÂÄÄÄÄÄÄÂÄÄÄÄÄÄÂÄÄÄÄÄCVTÄ> Ham /P shack
    230V? Other unknown intermittant loads Isolated 240V

    It worked OK that is, until someone turned on a small kettle (Diode load type!) that DC saturated the core!

    AS A SINE WAVE INVERTER
    Using the same magnetic arrangement, but starting with a square wave low voltage inverted input instead of the mains primary, then a simple inverter can give a regulated sine wave output, but the efficiency is low (70%).

    O/P 1ÄÄ¿ === ____ 50Hz
    )|| ||( ³Tuned
    +11-13V____)|| ||(_ÚÄÄ)ÄÄÄÄÄÄÄ230V
    Square )|| ||( === ñ10V
    50Hz Wave )|| ||(____³_______Sine Wave
    O/P 2ÄÄÙ ===

    WITH MOTOR DRIVEN VARIAC
    For really good regulation the mains can be preconditioned with a motorised variac.
    ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄ¿
    MOTOR - - - - - - - - - - - - MOTOR ³ÚÄÄÄÄÄÄÄÄÄÄÄÄ¿³
    / ³ ³ ³³ ³~~³ ³~~~³ ³³
    / )|| === ____ CONTROL ³³ ³ ³ ³CVT³ ³³
    LÄÄÄÄ>)||______ || ||( ³ ³ ³ ³³ ³--³ ³---³ ³³
    160- .)|| 210- )|| ||(_ÚÄÄ)ÄÄÄÁÄÄ)ÄÄÄÄ ³ÀÄÄÄÄÄÄÄÄÄÄÄÄÙ³
    290V stop)|| 250V )|| ||( === ³ 230V ñ2V ³ .--~~~--.(M)³
    )|| )|| ||(____³______³____ 0 - 6kW ³ / Varicac \ ³
    NÄÄÄÄÁÄÄÄÄÄÄÄÄÙ === ³|o--( o ) | ³
    VARIAC CVT ³ \ / ³
    ³ '--__--' ³
    ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙ
    A decision circuit drives the motor to set the output exactly at 230V after a second or so. The CVT has to try to take care of spikes & dips that the variac motor control loop can't follow.

    This arrangement takes care of changing losses due to varying loads too, & used to be the Bees & Eees for fussy valve gear on unknown mains.


    See my buls on "Variacs", "Maplin Mains Meter 2000MU-UK", "Portable Appliance Testing" & also "Mains Power Protection".


    Why don't U send an interesting bul?

    73 De John, G8MNY @ GB7CIP


    -----------------------------------------